Troy
My understanding is that 12.2v is 50% charge, when measured resting, I.e NOT under load. I would have no qualms taking a battery to 12.0v when it IS under load as I would expect that to recover to well over 12.2v after a test of 20 minutes or so.
When I start my diesel heater (which draws about 25A for thirty seconds or so) the voltage temporarily dips waaaaay down, so much so that sometimes it refuses to start!
I think also most fridge compressor controllers have a low voltage cut out set at around 11v. I assume this is set low to allow for the temporary dip in voltage whilst loaded?
Hope this helps
Graeme
#366, 1996
Sent from my iPad
> On 9 Dec 2021, at 22:59, Troy Dunn <troutwarrior at gmail.com> wrote:
>
> Joe
>
> 12.00V is a really low depth of discharge for any lead acid battery under
> load including AGMs. Consider using a higher voltage like 12.20V if you
> want to extend the life of your batteries.
>
> Regards
>
> Troy